Small crack in screed but cant change level of floor what can we do

UK Tiling Forum; Established 2006

Welcome to the UK Tiling Forum by TilersForums.com, built in 2006 by Tilers, run by Tilers.

View all of the UK tiling forum threads, questions and discussions here.

S

Spearce

A crack of about 2 metres long 3mm wide has appeared in our floor after the underfloor heating has been switched on. Screed is sand a cement mix by builder on site. Floor area 5 x 6 metres. Screed was drying without heating for 90 days. Heating switched up to temp gradually. The builder also doing the tiling has said this is normal for the floor and can be tiled on. We can not put additional height on the floor as matched with existing floor. Can we lay the stone marble tiles on this? There seems to be no further cracks or movement for the last few days. Any help will be much appreciated.
 
You will need to use something like Ditra matting, builder is wrong to say this is ok. And no you must not lay tiles straight onto that floor.
 
Last edited by a moderator:
A crack of about 2 metres long 3mm wide has appeared in our floor after the underfloor heating has been switched on. Screed is sand a cement mix by builder on site. Floor area 5 x 6 metres. Screed was drying without heating for 90 days. Heating switched up to temp gradually. The builder also doing the tiling has said this is normal for the floor and can be tiled on. We can not put additional height on the floor as matched with existing floor. Can we lay the stone marble tiles on this? There seems to be no further cracks or movement for the last few days. Any help will be much appreciated.

Absolutely not...unless you want the stone to crack also. You should be using an uncoupling membrane with stone on heated sand cement. The crack is most likely secondary shrinkage.
 
Definitely needs a crack isolation matting.
Due to your struggle with height i was was going to suggest you could try Mapei Mapetex matting as it is very thin but it cannot be used over cracks larger than 2mm so you would need to look at something like Dural's CI+.
 
Absolutely not...unless you want the stone to crack also. You should be using an uncoupling membrane with stone on heated sand cement. The crack is most likely secondary shrinkage.

can you tell us more about secondary shrinkage please alan ,why and how it can be avoided if it can mate :thumbsup:
 
Thank you for all these suggestions. I am still concerned about the height issue as the builder has laid tiles on an exsisting flooring already. No underfloor heating on that part. The completion of the tiles go into the new extension. Will there be enough space for the matting. Thanks again.
 
No he removed tiles in kitchen old part of the house and laid ontop of floor levelling compound.
 
can you tell us more about secondary shrinkage please alan ,why and how it can be avoided if it can mate :thumbsup:

When you add water to cement in a sand cement screed it undergoes two basic mechanisms which cause it to shrink. The first is that water evaporates and the second is the apid hydration of the cement. These cause the screed to shrink in its early life. This effect is called primary shrinkage. Coupled with lack of compaction which leads to intrinsic weakness in the screed these are the primary causes of early age cracking in cement based materials.

Once the screed has set and become rigid and has ostensibly dried there will always be some moisture present and as long as this is there the hydration reaction continues. This hydration coupled with carbonation of the screed means tha for very long periods (years and years in some instances) the screed continues to shrink very slowly. This causes further cracking over time. This is called secondary shrinkage.

The ways to minimise this sort of cracking are to ensure that the screed is cured properly initially, ensure that it is fully compacted and does not dry too rapidly. This way it can build up enough internal strength to overcome the effects of the shrinkage. Lastly it must be remembered that this secondary shrinkage will always occur regardless of you efforts so correct screed design ais also essential I.e. joints in the right places and bay sizes not over sized.

Polypropylene fibres can also help but these deal mostly with primary shrinkage.


Hope this helps although much oversimplified....... 🙂
 
A crack isolation membrane like Mapei Mapetex or PCI Pesilastic is only 0.5mm thick.
 
When you add water to cement in a sand cement screed it undergoes two basic mechanisms which cause it to shrink. The first is that water evaporates and the second is the apid hydration of the cement. These cause the screed to shrink in its early life. This effect is called primary shrinkage. Coupled with lack of compaction which leads to intrinsic weakness in the screed these are the primary causes of early age cracking in cement based materials.Once the screed has set and become rigid and has ostensibly dried there will always be some moisture present and as long as this is there the hydration reaction continues. This hydration coupled with carbonation of the screed means tha for very long periods (years and years in some instances) the screed continues to shrink very slowly. This causes further cracking over time. This is called secondary shrinkage.The ways to minimise this sort of cracking are to ensure that the screed is cured properly initially, ensure that it is fully compacted and does not dry too rapidly. This way it can build up enough internal strength to overcome the effects of the shrinkage. Lastly it must be remembered that this secondary shrinkage will always occur regardless of you efforts so correct screed design ais also essential I.e. joints in the right places and bay sizes not over sized.Polypropylene fibres can also help but these deal mostly with primary shrinkage.Hope this helps although much oversimplified....... 🙂
Surely using rebar in the screed is the best policy and avoids the majority of these sorts of cracking issues??
 
Last edited by a moderator:
Surely using rebar in the screed is the best policy and avoids the majority of these sorts of cracking issues??

rebar is not used in screeds , it's for concrete , and sound an inexperienced thing to say AJ, the most used metal reinforcing used was chicken wire ,but not really practised much these days .
 
I am always wary of screed mixed on site, ratios are often wrong, although it can be done correctly I prefare ready mix when possible.:thumbsup:
 
would a semi dry screed cope any better with the shrinkage as no where near as much water, and would it help limit secondary effects a long as compacted properly???
When you add water to cement in a sand cement screed it undergoes two basic mechanisms which cause it to shrink. The first is that water evaporates and the second is the apid hydration of the cement. These cause the screed to shrink in its early life. This effect is called primary shrinkage. Coupled with lack of compaction which leads to intrinsic weakness in the screed these are the primary causes of early age cracking in cement based materials.

Once the screed has set and become rigid and has ostensibly dried there will always be some moisture present and as long as this is there the hydration reaction continues. This hydration coupled with carbonation of the screed means tha for very long periods (years and years in some instances) the screed continues to shrink very slowly. This causes further cracking over time. This is called secondary shrinkage.

The ways to minimise this sort of cracking are to ensure that the screed is cured properly initially, ensure that it is fully compacted and does not dry too rapidly. This way it can build up enough internal strength to overcome the effects of the shrinkage. Lastly it must be remembered that this secondary shrinkage will always occur regardless of you efforts so correct screed design ais also essential I.e. joints in the right places and bay sizes not over sized.

Polypropylene fibres can also help but these deal mostly with primary shrinkage.


Hope this helps although much oversimplified....... 🙂
 
original screed IS SEMI-DRY, WHEN MIXED PROPERLY, and if LAID PROPERLY TO BS ,It SHOULD BE WELL COMPACTED , there are so many that think they can screed :yikes: ,that just pick-up the basics, ( builders ) then balls it -up, AJAKS must see lots of these jobs, i even look on line and see so-called pros talking rubbish,in the instructions :smilewinkgrin: ah well you get what you pay for :lol:
 
Surely using rebar in the screed is the best policy and avoids the majority of these sorts of cracking issues??

Sand cement screeds should be reinforced using either d49 steel mesh or polypropylene fibres with the latter being the more popular. These are only to help with plastic shrinkage cracking which is primary shrinkage. They will help to stabilise against long term cracking but will not prevent it entirely. The way to avoid shrinkage racking would be to not use cement I guess.
 
how would the argument for a very week mix be , we have laid screed as week as 1-5 1-6 , this helps with less cracking,or what about a bit of lime ? AJAX
 
how would the argument for a very week mix be , we have laid screed as week as 1-5 1-6 , this helps with less cracking,or what about a bit of lime ? AJAX

For domestic houses the above .
we only use polymer -modified screeds in the swimming pools we do now 1-3 strength
 
thank you all for this just got back from work and this is of great help. So to summarise at this stage the thinest matting I can find is best. Can the tile height be lost over the room size when the tiles laid. Or will we have to have a step. Or do we get the builder to do something else. I wish we could get the floor ripped up and started by somebody that knows what they are doing. We feel gutted as we trusted this builder who said he could do it.
 
just got back from work and some really good stuff from you all. thanks so much. To summarise. we now need to put down some sort of matting down. The thinner the better. If the height of this is to much for the exsisting flooring can this height be lost over the size of the floor. 6m x 4.5m. Wish we could get the floor ripped up and started again. We trusted the builder as he said he could do the job but know wish we got somebody that knew what they were actually doing. thanks again.
 
original screed IS SEMI-DRY, WHEN MIXED PROPERLY, and if LAID PROPERLY TO BS ,It SHOULD BE WELL COMPACTED , there are so many that think they can screed :yikes: ,that just pick-up the basics, ( builders ) then balls it -up, AJAKS must see lots of these jobs, i even look on line and see so-called pros talking rubbish,in the instructions :smilewinkgrin: ah well you get what you pay for :lol:

Yep......
 
how would the argument for a very week mix be , we have laid screed as week as 1-5 1-6 , this helps with less cracking,or what about a bit of lime ? AJAX


This becomes a trade off between strength and malleability. Malleability should ot be confused with flexibility. Old fashioned lime screeds were very weak essentially and they moved like billyo without cracking...Portland cement has a lot to answer for......

Pas long as thereis enough cement to coat the aggregate particles with cement paste so that it holds them together then the water cement ratio can be very low. Typically a water cement ratio of just 0.2 will give you a strong screed but unfortunately you would never compact it.
 
just got back from work and some really good stuff from you all. thanks so much. To summarise. we now need to put down some sort of matting down. The thinner the better. If the height of this is to much for the exsisting flooring can this height be lost over the size of the floor. 6m x 4.5m. Wish we could get the floor ripped up and started again. We trusted the builder as he said he could do the job but know wish we got somebody that knew what they were actually doing. thanks again.

NO need to rip it up. The crack can be repaired by using a simpl low viscosity epoxy resin to fillet. Then use an uncoupling membrane before tiling. Jobs a goodun
 
Just to add my tuppence worth, I agree with everything Ajax has said. There should be no reason to rip the screed out if it is sound. However, it is important to be sure that it has 'finished' cracking before carrying out the crack injection. If you repair the crack too early you may find another crack appearing elswhere in the floor.

Once the floor has been repaired there should be no issue tiling onto it, but a decoupling mat would be belt and braces to be safe.

Cement based screeds are perfectly ok for use with underfloor heating, the problem is that the screed is typically around 75-100mm deep and so takes a long time to fully dry out, if the heat is turned on too early the screed is force-dried and they don't have the same tensile strength as gypsum screeds so are much more at risk of cracking. That said, it does seem like your builder was trying to do thngs right!
 

Advertisement

Thread Information

Title
Small crack in screed but cant change level of floor what can we do
Prefix
N/A
Forum
UK Tiling Forum
Start date
Last reply date
Replies
26

Advertisement

Tilers Forums Official Sponsors

Thread statistics

Created
Spearce,
Last reply from
Tim@Larsen,
Replies
26
Views
7,036

Thread statistics

Created
Spearce,
Last reply from
Tim@Larsen,
Replies
26
Views
7,036
Back