Discuss Moisture Meter - Test Floor Screed Moisture Before Tiling in the America area at TilersForums. The USA and UK Tiling Forum (Also now Aus, Canada, ROI, and more)
DHTiling
Very true sandy but i saw a floor layer take a reading once and it was well within the standards and then he proceeded to lay the carpet.. 2 weeks later the carpet was damp... moisture deep down had not fully dried and the carpet made the floor sweat.. Hence the damp carpet..
This is my main reason for sweat testing.... but Damp meters of a good quality will do the job.. i have not disputed that.. just a lot of money for something a tiler would rarely use IMO..
tarkett85
the only way to test concrete subfloors is with a hygrometer like protimeter hygromaster, protimeter mms or tramex cmexpert either by drilling floor and putting in the plugs or with a hygro box. All other damp meters are for wood but caan be used on concrete to give you best places to test. Rh% is the measurement british standards dictate otherwise you're liable for a failed floor. This should be done for every job and takes minimum of 48 hours to test.
Ajax123
That's not right......not right at all.
Ajax123
THe British standards recommend exclusively the hair hygrometer. This is covered in annex a of bs8204:1:2003 and is referenced in several other standards. When we talk about British standards though we are talking about a guide to best practice. British standards don't "back up" anything. In fact there are areas of the industry which do not have a British standard associated with them at all. People place far too much reliance on British Standards especially when you consider that there are several elements to a floor which are covered in differing standards each in conflict with the others. British standards have no legislative or contractual authority in themselves. If you don't follow them they can't take you o court an due you.
Just because a test is not covered by a British standard does not make it an invalid test. You can measure the moisture in a concrete slab in several ways including a carbide bomb, an oven dried sample, an electronic resistivitity meter, hygro hoods, and several others.
A method simply has to yield accurate and repeatable results in order to be useable. Some of these non British standard methods are covered in other standard documents eg bba certification, European standards, ASTM standards, CSM standards, technical guidance documents and manufacturers standard methods etc etc etc....
TT Tiling
hi i have a £35 one ,not sure wot make ,but all i can say is that we had a guy turn up and do a test for us useing one that cost £2500 and it give the same reading my one did ,lol
Ajax123
I personally use two methods predominantly. The first is the tramex moisture encounter meter which works on both concrete and gypsum screed. About £500 worth so not something i would expect most tilers to have. The problem with this on gyp floors is that it can be misleading so you need o have a bit of experiencewith the floors so you can interpret the results. For this reason I always back up a result with an analogue surface hair hygrometer which is freshly calibrated after each use. I trust this method 100%. If the Tramex says its wet then I dont bother with the hygrometer as it is pointless. You can use digital hygrometers which ou can buy for about £80 but these work differently an can be prone to innaccuracy when outside the range about 70 to 85% so if ou get a reading of above 85% you can say its not dry but you can't accurately say by how much. The accurate range is fine though cos it spans the readings we want I.e. 75% and below for cement addy and 85% and below for gypsum addy.
Occasionally I will break out a sample or laboratory analysis and very occasionally use the polythene bag test as an indicator
Reply to Moisture Meter - Test Floor Screed Moisture Before Tiling in the America area at TilersForums.com
Apatel