Very very neat layout there @impish I like it
I don't why . They given you what they think is a legitimate reason for failure so why not say . As I said I had exact same problem with thermonet .
Lovely neat work impish question:
Where you have used duct tape to secure the cable in place, can you be 100% sure there are no voids between the cable and the tape? I'm just comparing my masking tape situation to your duct tape and TBH I cant see a difference
Nope. Can't be 100%. But I believe that the cables aren't the weak spots.
Tails and joints are. It's stressed by all manufacturers that those must be embedded.
I always flood my cables (and occasional mats) with slc which is a safer bet than adhesive straight on. Far fewer air pockets - tape or no tape I guess.
Main contractor who supplied heat mat paid for repair but asked me to go and replace Tile which I did . But until you have one of these situations you don't realise how critical some aspects of it are . Personally where possible I am going the use the system where the wires push into membrane to limit the amount of tape used like the Variopro systemWhat was the outcome ?
If I'm correct, they take a resistance reading between the cable core and the outer braid. (The metal strands that surround the core and core insulation.)Also does anyone know what this means- it was one of the notes on the bottom of the report
Resistance reading less than 999Mohms of heating element to braid (or earth) indicates heating element
insulation damage. Heating cable in working order although low resistance reading may deteriorate and cause future
failure. Fault location not attempted with element to braid (or earth) resistance above 10Mohms due to risk of damage
to heating cable. IEE Wiring Regulations require minimum insulation value of 1Mohm for general supply wiring
Also does anyone know what this means- it was one of the notes on the bottom of the report
Resistance reading less than 999Mohms of heating element to braid (or earth) indicates heating element
insulation damage. Heating cable in working order although low resistance reading may deteriorate and cause future
failure. Fault location not attempted with element to braid (or earth) resistance above 10Mohms due to risk of damage
to heating cable. IEE Wiring Regulations require minimum insulation value of 1Mohm for general supply wiring
They put a high voltage through the mat and used thermal imaging to detect the fault so I assume the original failure didn't look as bad as it did but by sending a high voltage through the mat it explodes at the weakest point and in this case was my taped over end join. Is this right ?
@thickbed can I assume that if we are still going on about this now, that they did indeed contact you before they went ahead with the repair and you refused to go look at the job or said it wasn't your job to or something and now you're just trying to pass the blame?
Reason I say this is because if you didn't have the chance to repair a fault of yours, or at least be involved in agreeing whether repair costs are appropriate, it's not something you need to carry on worrying about.
And you keep skipping past me pointing this fact out.
So I'm starting to think you perhaps did have the opportunity but avoided it maybe?
If that is the case, just split the bill with the builder and swallow your pride and move on.
But don't wriggle out of it.
Perhaps go on a UFH installation course and learn about it. Or avoid installing it in the future.