Interested in views from the trade world about how I should deal with a big floor tiling **** up. Basically I'm wondering how far I should be pushing my builder to put things right. I've had porcelain floor tiles laid dot-and-dab (sorry, you must all be so bored of that topic) over under-floor heating and am now nearing a dispute of whether several grands' worth of back-pedaling is needed to put the job right.
Bit of background on me on this sort of stuff. Not a pro in the building trade but not blowing my trumpet to say I'm pretty handy on most things around the house - basic repairs, medium size building work, plumbing, electrics, tiling, papering, plastering, and servicing the car until the things became so complicated that you don't recognise anything under the bonnet anymore. My missus says I'm a bit of a perfectionist but I just want to get things right as I don't like the idea of being a DIY botch merchant. Not the fastest in the world but I err on the safe side, ask when I don't know, and am prepared to rip it out and go back to the start when I've got it wrong - which as the years and experience go by is pleasingly rare. Big projects (loft conversion, extension, new central heating) I've had people in (time, effort, feeling older these days). I've had guys I've sacked off jobs when I know I could've done it better and guys I've just been blown away by. This is just to set the scene that I am not completely ignorant when talking to builders etc (relevance apparent later) and not prone to knocking tradesmen just for the sake of it.
Background on the mess I'm in now. Job was a kitchen extension - side return and old lean-to plus a few bits in the neighbouring utility room. Floor for old kitchen was and remains suspended timber, new floor to the side and end of this is concrete. Good job from the builder structurally, really good, would have him back but only for building. Part of the job price was laying the electric (loose cable) UFH and tiling the floor.
In December he laid the UFH cable then the tiles dot-and-dab. Looks like UFH absolutely beyond a doubt has to be laid in a bed (no previous personal experience). For the tiling, I have laid three floors - the old kitchen area twice and the utility room once. All three needed a power breaker to get them up. I'm not an expert but I know if getting them up doesn't break them, they weren't laid right. All mine were a sod to get up. I queried dot-and-dab method with the builder. Told me it'd be fine, done-loads-like-this-and-never-had-a-problem, plus floor not level etc. Apparently self-leveling compound wouldn't have been an option (?). Instinctively UFH cables surrounded by air struck me as pretty effective insulation (think secondary glazing, layers of clothes when it's cold) but he had some interesting ideas on hot air rising to the tiles that didn't really fit with my understanding of physics (I have a scientific background). Against better judgement and with time-constraints I was reassured that if there were any problems he would put them right. To be fair, he hasn't deserted yet.
Kitchen was then fitted on the floor - units along three walls with and an island. Stone work surfaces on top. Wasn't crazy money but far from the cheaper end of the market (that's my missus).
Floor was basically alright to begin with except that it sounded like walking on a xylophone with the different note of each tile with a void underneath. Then a tile started to knock when you stepped on where a dot was coming loose underneath, then another did it and so on.
To his credit he came round to look at it. I managed to dissuade him from his plan of drilling small holes around the edges of tiles and squirting in expanding foam to fill the void and adhere the tile. For me the insulation properties of the foam seemed a bad plan for UFH, and I wasn't convinced it would work anyway and managed to dissuade him on the lines of the possibility of hitting an UFH cable.
After some chats we agreed to try and get up some of the loose tiles. I offered to do that with him. After taking up a few it was apparent that it was only the grout keeping the tiles there. After cutting through the grout each tile lifted easily. Hardly a blob of adhesive has been left on the back of any tile - they look straight out of the shop (turns out he's not sure for certain what adhesive he used).
We just did a couple to start and I indulged him in his experiment to lay one by filing the void with expanding foam with Gripfill on the remaining adhesive dobs. Great experiment. It holds pretty well (but still sounds hollow) but the UFH beautifully heats where the dots are and the rest of the tile stays cold until the heat conducts through the tile. For anyone who lays UFH I'd be happy to chit-chat on some of what I'm seeing that absolutely confirms manufacturers' fitting instructions - except it should all be pretty obvious, it's a bit like bothering actually to test jumping from a plane without a parachute (never formally tested but we all know the result).
We agreed to lift all those that we could without disturbing the kitchen units and did so without damaging the UFH (they come up that easily).
There is/was a plan to remove some of the dots for each tile, leaving a dot at each corner so that a bed of adhesive could be laid in the remaining space but with the dot keeping the level for relaying with Gripfill on top of the old dots to hold the tile at those points. For tiles not lifted because they extend under kitchen units' end panels, they've have expanding foam squirted under (no UFH there) to fill the void, then as much adhesive pushed under as can be achieved, to hold the edge .
Last night after many hours of dissecting dots and dabs away from UFH cable and off the foam insulation tile backer boards stuck to the sub-floor, I started to lose it. In parts of the floor, the insulation is tearing badly and where foam has been squirted under less-accessible tiles, I can't hear a difference when I knock on them. Some of the dots that are due to have Gripfill on them knock against the floor beneath so, presumably lifting the tiles, however easy, is disturbing the adhesion between the sub-floor and the insulation boards. Gripfill on these dots is always going to knock unless by luck it gets held by enough adhesive around it.
This is about where I lost it. None of this is right. I'm looking at hours of work, much of which I have offered to do (not fundamentally opposed to that), in which I have decreasing confidence of an effective, long term outcome, for which I paid and questioned when it was in progress.
That was a long preamble but here is my dilemma. I am increasingly coming to the view that there is no way to get it right than to go back to where things started to go wrong. To do that I can't see a way other than dismantling the installed kitchen, getting the tiles up, leveling the floor (might include grinding off adhesive for the insulation boards), then UFH with insulation, tiling the floor and reinstalling the kitchen. I have suggested this but it is understandably not well received. I have indulged/am still indulging in his suggestions of how to right things but I'm wondering if this is just pissing in the wind.
I do get my builder's reluctance. Shifting the kitchen will need to shift the stone work tops. It's likely these will break (cut for cookers, sink etc). I'd not be surprised that getting back to a floor that can be done properly will cost 2-3 grand for kitchen dis-assembly/assembly, 2 grand for work tops if they can't be saved, couple of hundred for insulation board, and around 700 for UFH cable. I'm not worried on a grand's worth of tiles - they're a doddle to get up as nothing's holding them. I get the costs involved of going right back to get it right but I'm looking at around 25k of units and kitchen machines, in a project that cost around 70-80k. Without fitting (which was in the price), the UFH and tiles come to less than 2k - which bit would I want to save?
What thoughts from the trade? How much more should we try foam, pushing in proper adhesive, prayer, pixie dust? When is it reasonable to draw a line and say that we go back to where the wrong turn was taken, whatever the costs? Who should incur those costs? Am I being unreasonable or unreasonably fussy? Despite the numbers above, I'm not loaded - I took out a mortgage to do this and I'll be paying it forever.
Finally if anyone's got a great idea, I'm all ears.
Thanks if you bothered to read this far
Regards
Matt
 
  • Like
Reactions: Dan
OP
M

My dog's called Trevor

Well you must be right 3_fall as I'm back for more.
Anyone got any thoughts on an expansion joint between the timber floor and the concrete slab? The dimensions in

Sorry. Keep hitting the post button when I do this on my phone.
Is the expansion joint a bit of a recommendation or is it like whether you should have oil in your gearbox? I've dipped into the BS 5385 (not bought one for that price - costs more than a Gutenberg Bible). Does reckon you should have one when spanning different surfaces but I bet there're loads of jobs like mine where there isn't one. Looks like the joint would need to be at tile level although I've seen some US sites talking about something that goes over the joint to prevent cracking.
Reckon it will need discussing with the builder tomorrow
Thanks all
Matt
 

cam_low

TF
Supporter
Reaction score
193
I would be advising on using a heating system like that of ditra heat-e or the new thermonet similar system, I would also use a grout colour matching silicone for the joint, hopefully you can set the tiles out along that line to keep full tiles.
 
OP
M

My dog's called Trevor

I would be advising on using a heating system like that of ditra heat-e or the new thermonet similar system, I would also use a grout colour matching silicone for the joint, hopefully you can set the tiles out along that line to keep full tiles.

Many thanks Cam
Will look into those systems. Depending on how straight and square in the corner the old wood floor is, it might be possible to line them at the joint
Thanks again
Matt
 

Dan

Admin
Staff member
Reaction score
6,137
I'd go with the expansion joint and also don't cross cable over the joint. Run the two mats / cables to a junction box (only have cold cable not in the adhesive) and then from the JB to the thermostat. Might need advice from a sparky about that. We have a sparky forum. Link in my sig'.

You don't want the hot cable spanning two different substrates.

If also not wing it by avoiding an expansion. You've done all the winging it that you can on this one.

The matting on US sites might be uncoupling membrane. Dural C++ or Ditra are two brand names.
 
OP
M

My dog's called Trevor

Could do with some good photos of the floor , but if you have some decent photos of women in bikini's thats always welcome :):bikini:

Thanks Widler
Could pull the cardboard up tonight and get some pics. Think it's not going to show the joint as it's got the insulation board down. Basically just going to show the glorious extent of the dot and dab and uncovered UFH cable - but I expect that's worth it to give everyone a chuckle.
On women in bikinis, will this do?
 

Attachments

  • I'm Stuck - Wish My Tiles Were | TilersForums.com Filename: {userid}
    image.jpg
    35.6 KB · Views: 27
OP
M

My dog's called Trevor

I'd go with the expansion joint and also don't cross cable over the joint. Run the two mats / cables to a junction box (only have cold cable not in the adhesive) and then from the JB to the thermostat. Might need advice from a sparky about that. We have a sparky forum. Link in my sig'.

You don't want the hot cable spanning two different substrates.

If also not wing it by avoiding an expansion. You've done all the winging it that you can on this one.

The matting on US sites might be uncoupling membrane. Dural C++ or Ditra are two brand names.

Thanks Dan
Really helpful
Matt
 
OP
M

My dog's called Trevor

Thanks Widler
Could pull the cardboard up tonight and get some pics. Think it's not going to show the joint as it's got the insulation board down. Basically just going to show the glorious extent of the dot and dab and uncovered UFH cable - but I expect that's worth it to give everyone a chuckle.
On women in bikinis, will this do?

Amazing the 'Likes' just for a photo of some semi-naked fat birds.
 

Reply to I'm Stuck - Wish My Tiles Were in the Tiling Forum area at TilersForums.com

Similar threads

What would cause algae and should I be concerned?
Replies
3
Views
265
I'm redoing our bathroom and looking for some advice on tiling backer boards in relation to the external masonry...
Replies
0
Views
843
Order of Events: Your proposed order seems well-researched and generally aligns with best practices. Ensuring the...
Replies
5
Views
905
Its the kitchen but you are right. I did wonder if the thin back buttering stuck to the dabs but came away from the...
Replies
8
Views
606
Thanks. It's done - pretty much as I planned but I made a 15mm notched trowel from an old float. I back buttered the...