BG Split load board 18th edition compliant? Electrical Advice

Tilers Forums Official Sponsors

BG Split load board 18th edition compliant? Discussion ThreadBG Split load board 18th edition compliant? Electrical Advice

6 Way Metal Dual Split Consumer Unit c/w 2 RCDs (Type A) c/w 6 MCBs | BG (CFUDP16606A-01)

BG are stating that these are 18th edition compliant. I'm doubtful if they meet regulations 536.4.3.2 & 536.4.202 - overload protection of switches and RCCBs.

the RCDs are rated at 63A. There is no way of configuring the supplied MCBs that doesn't exceed 63A.

I guess if the main fuse was 60A it might be compliant but then would there not be an issue with the potential load of the installation being > 60A causing the DNO fuse to blow?

BG Split load board 18th edition compliant? for the original thread on Electricians Forums
 