I was replacing a socket that had a cracked face and as I took said socket off I noticed the armour was earthed by using BS951 clamps. I wasn’t expecting to see any earthing of the armour as the SWA was in a conduit drop to the socket.

I’ve never seen it done like that before but now I walk around the factory and automatically assume every SWA I see entering a conduit drop will have the armour earthed with the clamps. Never been referenced on any EICRs we’ve had done in the past.

I don’t like it as the SWA hasn’t been glanded, just been shoved down the conduit.

I took the conduit drops away and glanded the SWA appropriately with the use of Earth Nuts.

Is the use of BS951 clamps acceptable practice for the earthing of armour?

[ElectriciansForums.net] Earthing Armour with BS951 clamps?


Earthing Armour with BS951 clamps? for the original thread on Electricians Forums
 