Hi. I have a sand and cement screed (75mm deep) with wet underfloor heating installed. The screed will be 5 weeks old when tiles are planned to go down. The underfloor heating will have been run up to temp and down over the 5th week. I'm currently getting quotes to tile it. I've read that a de-coupling mat should be used but as with most things in life everyone seems to have different opinions :lol: We have chosen a modular porcelin tile. The only thing that is agreed on is that the screed isn't a great level so they all want to latex it first. As the rest of the downstairs is being latexed due to a poor original screed it's no big deal to get the kitchen done at the same time.

Any advice on drying times and the use of a matting would be really helpful.

Many thanks


 
A

adros88

Thanks everyone for the advice. I've been using this site for a while and got loads of useful advice from other posts. I've had two tilers round to quote (did try for 3 but got stood up by the first two i booked to meet!) Neither of them mentioned matting until I brought it up. They didn't seem too bothered about putting it in but I think I'm going to insist on it.

The new screed only meets the old at the door way between the hallway and the new kitchen floor, so the ditra can start flush with the door.

Does the extra adhesive used to lay the matting make much difference to the UFH performance?
 

Ajax123

TF
Esteemed
Arms
931
1,213
Lincolnshire
Uncoupling is not essential however in line with the other recomendations and for the sakeof the relatively small cost in comparison to the possibility of the screed cracking and causing a tile I also I think I would go for it on this type of screed.

I am concerned that ou think that you can run the heating up to temperature and down again ready for tiling in a single week. To do this properly and despite the advice given in the British standards which is very poor this runup and down should be gradual. Switch on at ambient and leave for three days, increase by max 5 degrees per day up to maximum temperature, leave at this for three days then reduce the temperature by the same maximum 5 degrees per day then switch it off for three days prior to moisture testing and finally tiling ifit is dry enough. Any quicker than this and you could well end up with crazy paving.
 

Reply to does wet UFH need ditra matting??? in the UK Tiling Forum area at TilersForums.com

Posting a tiling question to the forum? Post in Tilers' Talk if you are unsure which forum to post in. We'll move it if there's a more suitable forum.
Please visit our sponsor websites, they keep the forum free to use!

Advertisement

Replies you've not seen

You're browsing the UK Tiling Forum category on TilersForums.com, the tile advice website no matter which country you reside.

Top