Electrical Advice

Moving CU away from service head. SPD at the fused switch or DCU? Electrical Advice

Moving CU away from service head. SPD at the fused switch or DCU? Discussion ThreadMoving CU away from service head. SPD at the fused switch or DCU? Electrical Advice

I'm moving my CU away from the service head. About 8m in 25mm2 SWA. Do I need to put an SPD T2 at the 100a fused switch I'm installing or can I get away with just having one at the new CU location? I'm struggling to find options for the service head location. They a lot more expensive and the box is bigger, smaller...
 

tridonic switchdim ballast Electrical Advice

tridonic switchdim ballast Discussion Threadtridonic switchdim ballast Electrical Advice

i was just looking at a job today, where the push switch on the wall had the feed coming into "com" and a brown in " L1 " and blue " L2" when i took the light down it had a brown in "D1" and blue in "D2" is it possible to apply 240 volts to both those connections on the ballasts or is "D2" always neutral??

tridonic switchdim ballast for the original thread on Electricians Forums
 

ZS testing - dangerous? Electrical Advice

ZS testing - dangerous? Discussion ThreadZS testing - dangerous? Electrical Advice

I have read somewhere that performing a zs test where there is exposed metalwork and people around can be dangerous? Is it something that has to be avoided? Or does it say anywhere that it must not be done? Should i be worried about carrying out Zs tests now? :/

ZS testing - dangerous? for the original thread on Electricians Forums
 

R2 test without removing cover Electrical Advice

R2 test without removing cover Discussion ThreadR2 test without removing cover Electrical Advice

Hi all when performing an r2 test prior to commencing an EFLI test would it be acceptable if the board was made from metal of course to test from the point to the outside of the board rather than to the earth bar? Just for when you are working with large 3phase boards full of cables.

R2 test without removing cover for the original thread on Electricians Forums
 

Signal generator amplifier using only positive pole output, underperforming Electrical Advice

Signal generator amplifier using only positive pole output, underperforming Discussion ThreadSignal generator amplifier using only positive pole output, underperforming Electrical Advice

I have a 100W 50 ohms signal generator amplifier with a 35 meters coil wire (1.5 mm) as a load, BNC connectors. The requirement is that only the BNC POSITIVE pole is connected to the wire and used as antenna. The amplifier require a minimum of 4 ohms load. This is not a closed circuit antenna...
 

Circuit design for computer circuits. Electrical Advice

Circuit design for computer circuits. Discussion ThreadCircuit design for computer circuits. Electrical Advice

Hi Guys,

I'm currently designing an installation that will be used to configure multiple pieces of electronic equipment such as PC's, Servers, All in ones etc. Its going to be set up in bays such as the picture attached. With it being a full socket installation I was hoping for some guidance if I'm approaching the maximum demand calculations correctly with diversity. There...
 

Clear up a bonding debate of ours. Electrical Advice

Clear up a bonding debate of ours. Discussion ThreadClear up a bonding debate of ours. Electrical Advice

Hi all
Wondered if you could clear up a debate we are having at work.
Gas inspection has said no bonding to the gas meter or pipe in block of flats.

One engineer says it should be run to the meter.
One says it should be installed outside within 600mm of where it enters the building on the blue arrow.
And one engineer says it should be inside 600mm from where it enters the flat...
 

Local RCBO protecting ring final alteration. Electrical Advice

Local RCBO protecting ring final alteration. Discussion ThreadLocal RCBO protecting ring final alteration. Electrical Advice

Hi
I completed a job recently where a hotel reception had a new desk fitted. The old desk dado was supplied via an RCD spur from the existing ring. This ring is fed from one of the very old Merlin single phase boards which I’ve been told you cannot retrofit Schneider ic60n RCBO’s in. I had to remove a couple of sockets including the existing Rcd spur from a...
 

Light switch replacement (lights flickering) Electrical Advice

Light switch replacement (lights flickering) Discussion ThreadLight switch replacement (lights flickering) Electrical Advice

Hi,

Friend asked me to check out their light switch cause the kitchen lights were flickering and the faceplate was getting hot. They sent the photos below to show what it looked like, obvious issue is the common looking fried, which I put down to a loose connection, hence the flickering lights.

To replace the front plate, all the old wires go in the same...
 

Generator to run oil fired boiler or immersion heater? Electrical Advice

Generator to run oil fired boiler or immersion heater? Discussion ThreadGenerator to run oil fired boiler or immersion heater? Electrical Advice

Hi. We've a champion generator, inverter, dual fuel, 3.6 kw, which we've used a couple of times during power outages over the last 18 months to power a fridge (class 1) - needed to keep my partner's meds. at fridge temperature and a range of other items (class 2) such as broadband router, TV, radio, a couple of standard lamps. Simple system...
 

Diversity on a 20 Way or longer CU with many (low utilisation) ring mains Electrical Advice

Diversity on a 20 Way or longer CU with many (low utilisation) ring mains Discussion ThreadDiversity on a 20 Way or longer CU with many (low utilisation) ring mains Electrical Advice

Hello,

A quick question which I suspect is becoming more commonly asked as we go towards having more ways in our CUs.

Domestic dwelling, nothing too exuberent but during rejigging the large downstairs ring was split into three and some radials added, as well as seperate feeds to allow for a...
 