Maximum Zs Value Exceeded Electrical Advice
- By Lou
Maximum Zs Value Exceeded Discussion ThreadMaximum Zs Value Exceeded Electrical Advice
Hi
I have recently done some testing on an installation. A submain is fed from a B50 mcb and has a zs of 1.10ohms. The maximum for this is 0.87. The cable supplying the submain is a 25mm 2 core swa with the armourings used as the cpc and is roughly a 70m run. Both glands and earth leads have been checked and are okay.
Would it be viable to fit a 300ma rcd to protect this circuit as the...
Hi
I have recently done some testing on an installation. A submain is fed from a B50 mcb and has a zs of 1.10ohms. The maximum for this is 0.87. The cable supplying the submain is a 25mm 2 core swa with the armourings used as the cpc and is roughly a 70m run. Both glands and earth leads have been checked and are okay.
Would it be viable to fit a 300ma rcd to protect this circuit as the...