Screed \ Under floor heating advice

Discuss Screed \ Under floor heating advice in the Canada Tile Advice area at TilersForums.com.

Hi,

We have had a screed (anyhdrite) with wet underfloor heating put down recently. After a few weeks they turned on the heating and then after a few days a small dark spot appeared, this grew in size to a 10cm elongated circle. There is metal pipe coupling directly below.

We suspected a leak.

Anyway, we had the contractor back today, and he said it was n't a leak as it would be a circular shape if leaking.

That does n't sound right to us. Does anyone have an experience of this? What else could explain it?

Thanks,
 

Attachments

  • screed_leak.jpg
    83.3 KB · Views: 41

Dan

Admin
Staff member
5,045
1,323
Staffordshire, UK
How many weeks? And was the heating commissioned correctly?

You have to bring it up to temperature slowly, then leave it on full 24 hours, then bring it back down a degree or two per day to cold. Then it can be used as you wish.

Without doing that process you stress the system and the floor.

You have a leak for sure. That's wet right? Did the contactor pressure test it?
 
How many weeks? And was the heating commissioned correctly?

You have to bring it up to temperature slowly, then leave it on full 24 hours, then bring it back down a degree or two per day to cold. Then it can be used as you wish.

Without doing that process you stress the system and the floor.

You have a leak for sure. That's wet right? Did the contactor pressure test it?
[automerge]1575315567[/automerge]
Screed was down for 3 or 4 weeks before the heating was turned on. Heating was turned up to 40oC was commissioned, and has not been brought back down..

Yes, look wet to me too.

Pipes and screed were put down in one day, so not a long pressure test if any.
 

Ajax123

TF
Esteemed
Arms
931
1,213
Lincolnshire
There are proprietary joints for UFH pipes but the preference is always jointless. This doesnt look like a leaking pipe though. it is too concentrated. In a screed the water would spread much more especially in anhydrite. Unless the pipe is very close to the surface.... I think it needs further investigation. Does the dark patch feel wet to the touch?
 

Ajax123

TF
Esteemed
Arms
931
1,213
Lincolnshire
Thanks All.

The patch is expanding slowly now. There has been no rain and there are not any pipes above it.

When the contractor came he said that the coupling was quite close to the surface.
Ah well if it is indeed expanding slowly leak it probably is... it needs excavating and affixing properly then. Was the system not pressure tested properly before screeding?
 

Reply to Screed \ Under floor heating advice in the Canada Tile Advice area at TilersForums.com

There are similar tiling threads here

I had a small leak in the main water line before the stop tap in my 1950s house. The copper pipe had worn away over the past 70 years, causing a small crack in the copper. A plumber/builder fixed...
Replies
1
Views
862
Hello there, Relatively recently we had a new en-suite fitted (complete rip out of the old fittings, and old wall tiles and floor carpet). This consisted of a quadrant shower enclosure, a...
Replies
5
Views
2K
Posting a tiling question to the forum? Post in Tilers' Talk if you are unsure which forum to post in. We'll move it if there's a more suitable forum.

Advertisement

Top