Hello! Please I need your help. I'm living in a 3yo department on a 5th floor (the entire building is 14floors). 3 months after moving in I noticed hairline cracks on more than 10 floor tiles, some of them linear and comprising 3/4 adjacents tiles. Others, just randomly on one isolated tile. I had them replaced, but a year later discovered the same problem: many of the repaired tiles had THE EXACT SAME CRACK in the exact same place (linear, including 3/5 adjacents tiles). Had them replaced again and now, after 6 months of the last replacement, I found that same linear hairline crack is appearing on THE SAME REPLACED TILES and following the same direction. Cracks are almost imperceptible (just able to see the if I bright a light on them). But I'm very concerned. The builder company says it's normal for a big building to move and to have some cracks but I'm super worried. Why is it that they happen to be always in the same place/tile and following the same direction? May this indicate a structural problem?

I would really apreciate your help. Try to attach some pictures. Thank you in advance
 

Attachments

  • tKcj4HRQ8z.jpg
    tKcj4HRQ8z.jpg
    110.3 KB · Views: 36
  • IMG_20211014_175631.jpg
    IMG_20211014_175631.jpg
    176.6 KB · Views: 35
N

Nathan Walker

Tiler most probably hasn't prepared the floor correctly, an uncoupling sheet/crack mat should have been installed to prevent cracks forming due to movement of the floor. In my opinion needs ripping out and starting again from fresh.
 
Upvote 0
Reaction score
0
Tiler has most probably not used an uncoupling sheet/crack mat when preparing the floor for tiling, this prevents cracks forming from movement and settling of the floor over time. Please see attached photo of said matting.
 

Attachments

  • IMG_20210923_102613.jpg
    IMG_20210923_102613.jpg
    1 MB · Views: 32
Upvote 0

Dave

TF
Staff member
Esteemed
Supporter
Arms
Reaction score
18,448
:)
Hello! Please I need your help. I'm living in a 3yo department on a 5th floor (the entire building is 14floors). 3 months after moving in I noticed hairline cracks on more than 10 floor tiles, some of them linear and comprising 3/4 adjacents tiles. Others, just randomly on one isolated tile. I had them replaced, but a year later discovered the same problem: many of the repaired tiles had THE EXACT SAME CRACK in the exact same place (linear, including 3/5 adjacents tiles). Had them replaced again and now, after 6 months of the last replacement, I found that same linear hairline crack is appearing on THE SAME REPLACED TILES and following the same direction. Cracks are almost imperceptible (just able to see the if I bright a light on them). But I'm very concerned. The builder company says it's normal for a big building to move and to have some cracks but I'm super worried. Why is it that they happen to be always in the same place/tile and following the same direction? May this indicate a structural problem?

I would really apreciate your help. Try to attach some pictures. Thank you in advance
What is the subfloor constructed from ?
 
Upvote 0
OP
T
Reaction score
1
:)
Tiler most probably hasn't prepared the floor correctly, an uncoupling sheet/crack mat should have been installed to prevent cracks forming due to movement of the floor. In my opinion needs ripping out and starting again from fresh.
Thank you! They didn't use any mat. But appart from the cracks do you think it could be an structural problem? As they keep appearing on the right exact place...
 
Upvote 0
J

Johnno

You should expect any building to expand & contract with changes in temperature and humidity .think of it as a living entity..it has to breathe to survive..it it didnt it would eventually fail..these contractions and expansions are minute but happen in all structures no matter what they are made from.
Has a flexible floor adhesive and grout been used to secure your tiles ?
Although I have never suffered this problem after an install I have had grout break out due to excessive movement of the sub floor..next time your tiles are replaced ensure a ' super flex ' adhesive is used and possibly a flexible ad mix to boost the flexibility of the adhesive..the install I had problems with I used both, a super flex tile adhesive ( powder so you can mix it yourself & add the flex additive ) and same for the grout. This route solved the issue I had and hopefully will resolve those you are having
 
Upvote 0
J

Johnno

:)a building has to breathe..by that I mean expand and contract as the temperature and humidity changes , any movement is only minute but they are built to do just that..they would simply fall apart if they didnt...I would suggest the sub floor below the tiles cracking is prob flexing moving slightly more than elsewhere and the tiles are fixed too firmly across that area so cracking.
Ensure a ' super flexible ' adhesive is used next time they are replaced. You could also add a flexible additive to give it extra flex ( make sure it's a powder mix not ready mixed out of a tub ) then you can use the additive to provide that extra bit of flexibility.
I've only ever had problems with grout breakup g out due to subfloor movement and although used a flexible grout , the sub floor movement was still too much so when re grouting used some additive..problem solved..you will probably find that your installer have not used a flexible adhesive because your sub floor is a concrete slab and unlike a timber sub floor , you dont expect it to flex / move in any way, whereas a timber sub floor can move / flex quite a bit..
Hope this helps
 
Upvote 0
OP
T
Reaction score
1
:)
You should expect any building to expand & contract with changes in temperature and humidity .think of it as a living entity..it has to breathe to survive..it it didnt it would eventually fail..these contractions and expansions are minute but happen in all structures no matter what they are made from.
Has a flexible floor adhesive and grout been used to secure your tiles ?
Although I have never suffered this problem after an install I have had grout break out due to excessive movement of the sub floor..next time your tiles are replaced ensure a ' super flex ' adhesive is used and possibly a flexible ad mix to boost the flexibility of the adhesive..the install I had problems with I used both, a super flex tile adhesive ( powder so you can mix it yourself & add the flex additive ) and same for the grout. This route solved the issue I had and hopefully will resolve those you are having
Thank you very much for your time..I will do this
 
Upvote 0
OP
T
Reaction score
1
:)
Tiler most probably hasn't prepared the floor correctly, an uncoupling sheet/crack mat should have been installed to prevent cracks forming due to movement of the floor. In my opinion needs ripping out and starting again from fresh.

Hi! I need your help again please. I'm due to remove this 3 cracked tiles which have cracked for the third time after having replaced them 3 times. I'm not planning to re-tile the entire floor but just the 3 always-cracking-tiles. What would you recommend to do? What should I install below those 3 tiles to prevent cracks forming, considering that the floor around it won't be touched? If I use an uncoupling sheet for them it won't be levelled in relation to the rest of the floor. What do you think?
 
Upvote 0
OP
T
Reaction score
1
:)a building has to breathe..by that I mean expand and contract as the temperature and humidity changes , any movement is only minute but they are built to do just that..they would simply fall apart if they didnt...I would suggest the sub floor below the tiles cracking is prob flexing moving slightly more than elsewhere and the tiles are fixed too firmly across that area so cracking.
Ensure a ' super flexible ' adhesive is used next time they are replaced. You could also add a flexible additive to give it extra flex ( make sure it's a powder mix not ready mixed out of a tub ) then you can use the additive to provide that extra bit of flexibility.
I've only ever had problems with grout breakup g out due to subfloor movement and although used a flexible grout , the sub floor movement was still too much so when re grouting used some additive..problem solved..you will probably find that your installer have not used a flexible adhesive because your sub floor is a concrete slab and unlike a timber sub floor , you dont expect it to flex / move in any way, whereas a timber sub floor can move / flex quite a bit..
Hope this

Hi! I need your help again please. I'm due to remove this 3 cracked tiles which have cracked for the third time after having replaced them 3 times. I'm not planning to re-tile the entire floor but just the 3 always-cracking-tiles. What would you recommend to do? What should I install below those 3 tiles to prevent cracks forming, considering that the floor around it won't be touched? If I use an uncoupling sheet for them it won't be levelled in relation to the rest of the floor. What do you think?
 
Upvote 0
OP
T
Reaction score
1
Tiler has most probably not used an uncoupling sheet/crack mat when preparing the floor for tiling, this prevents cracks forming from movement and settling of the floor over time. Please see attached photo of said matting.
Hi! I need your help again please. I'm due to remove this 3 cracked tiles which have cracked for the third time after having replaced them 3 times. I'm not planning to re-tile the entire floor but just the 3 always-cracking-tiles. What would you recommend to do? What should I install below those 3 tiles to prevent cracks forming, considering that the floor around it won't be touched? If I use an uncoupling sheet for them it won't be levelled in relation to the rest of the floor. What do you think?
 
Upvote 0

Ajax123

TF
Esteemed
Supporter
Arms
Reaction score
902
you need to figure out why they keep cracking. they have cracked 3 times in the same place. something is happening to cause that. If you dont fgure hat out and fix it then youll simply end upwith tiles cracking a 4th time. .
 
Upvote 0

Reply to Help me with repeatedly floor cracked tiles PLEASE in the UK Tiling Forum | Tile Advice Forum area at TilersForums.com

Similar threads

  • Question
Hello. I need your help again please. I'm due to remove this 3 cracked tiles which have cracked for the third time after having replaced them 3 times (picture). I'm not planning to re-tile the entire floor but just the 3 always-cracking-tiles. What would you recommend to do? What should I...
Replies
4
Views
287
  • Question
I had ceramic tile installed and 6 months later I noticed cracks in about a dozen tiles. The cracks form 2 straight parallel lines 3 ft apart. The contracter says it is a high traffic area and the tile I chose was poor quality. The store says the tile is good quality and that it wasn't...
Replies
4
Views
373
  • Question
We recently had an en suite fitted by a local company that appears to be generally reputable. We've had a few issues with the work, one of which was that we noticed a hairline crack in one of the newly placed floor tiles. The company sent someone out to replace the tile and although I didn't...
Replies
13
Views
2K
  • Question
Had a tiler in to tile a living room (12m2). Bought the tiles ourselves. Came home to the job done and noticed slight colour variants in the tiles laid down. Pointed it out to the tiler who said he had noticed the differences in the tiles but the codes on the tiles were the same so he kept...
Replies
11
Views
573
  • Question
Hi guys, I need some advice here. I'm pricing a job that requires tiling a floor over existing tiles. The existing tiles have started to crack and move in some places, and the floor looks uneven so it will require some levelling prior to tiling over. The customer doesn't want to remove the...
Replies
5
Views
895
Tiling Courses
Workwear for Tradesmen
Mapei Tile Adhesive and Grout
uHeat
The Wetroom Store for all Wetroom Installations
Nicobond Tile Adhesives and Grout

Latest 10

Thanks for visiting TilersForums.com, formerly known as TilersForums.co.uk.

Search Forum

Top